RE: Superheat for a Marvair 48K wall pack system with a piston?

So what should my target superheat be with a R22 or MO99 system? Marvair compac 1 48K with a piston? I talked to marvair they are telling me 10-12 for superheat and 12-18 for subcooling. I was under the impression w piston was good for 20 degree superheat.

rick1981 Rookie Asked on June 15, 2018 in Commercial HVAC.
Add Comment
1 Answers

I had to download the I&O manual to see what this was.

 

Usually with a fixed orifice, I use a superheat calculator that can be downloaded and enter my Indoor Wet Bulb and Outdoor Dry Bulb temperatures and determine my superheat from there.

 

In my mind, a fixed orifice is a fixed orifice and must comply with the rules, regardless of what type of system it’s installed in. So I have no clue how the manufacturer can determine a generic superheat value.

 

But on the other hand, I’m not super familiar with the equipment but it looks like a window shaker had a really large baby…lol.

 

 

Rookie Answered on June 23, 2018.